The message below explains what happened. Again, my apology to users.

---------- Forwarded message ----------
From: Support Department <support@nocix.net>
Date: Fri, Jul 22, 2016 at 12:10 AM
Subject: Server down

At about 3:45 local time we experienced a complete loss of utility power. At that time we switched to generators. While on generators a capacitor in UPS 1 exploded. Once utility was restored, UPS 1 did not successfully handle the transfer and dropped its load causing a partial power outage on the data center floor. At this time, power has been restored to all affected servers and Eaton personnel are onsite effecting repairs the the damaged unit. We plan to have full UPS coverage restored in a few hours.